Points > Point Editor > String Properties
Click here to go to help for the General tab. Click here to go to help for the History tab. Click here to go to help for the Point reference tab. Click here to go to help for the Comments tab. Click here to go to help for the Application tab.

String Point Properties

Use the String page to configure string properties for a particular point. The String page is shown when the point type is set to String Input or String Output in the General page.

Point Properties String page
Sample String page for an Existing Point

String Properties

These are the properties shown on the String page in the PNT Editor. See also the ALARMSET security event for more information.

See Token Categories - Point: Alarm for the corresponding tokens for each property and Filter Attributes - Point: Alarm for the corresponding filter attributes for each property.

Property Description Default Value

Point scheme

Read-only. This value is set on the General page.

Point data type

Read-only. This value is set on the General page.

Alarm category for point

Select the alarm category for the point. Click to select a table entry. The entry comes from the PNTALCAT table.

Blank

Suppress alarms

Enables or disables suppression of alarms for the point and the suppression ending condition(s). Click to configure Alarm Suppression.

See also the ALMSUPP security event for more information.

0 (No)

Table Columns

Enable CVS Calculation

String Alarm 1 Enabled

String Alarm 2 Enabled

String Alarm 3 Enabled

String Alarm 4 Enabled

String Alarm 5 Enabled

String Alarm 6 Enabled

Enables the alarm bit. Options are 0 (No) or 1 (Yes). The alarm bit can be enabled without the Report Alarms flag set.

In the CygNet Standard Point Scheme, the alarms correspond to the following bits and alarm calculation types:

String Alarm 1 Configurable Bit 1 String Filter
String Alarm 2 Configurable Bit 2 String Filter
String Alarm 3 Configurable Bit 3 String Filter
String Alarm 4 Configurable Bit 4 String Filter
String Alarm 5 Configurable Bit 5 String Filter
String Alarm 6 Configurable Bit 5 String Filter

See also the CFGBITxx security event for more information.

0 (No)

Calculation Value 1

String Alarm 1 Calc Value 1

String Alarm 2 Calc Value 1

String Alarm 3 Calc Value 1

String Alarm 4 Calc Value 1

String Alarm 5 Calc Value 1

String Alarm 6 Calc Value 1

The alarm setpoint. Setpoints are case sensitive. Single character (?) and multi-character (*) wildcards are supported.

Blank

Alarm Priority

String Alarm 1 Priority

String Alarm 2 Priority

String Alarm 3 Priority

String Alarm 4 Priority

String Alarm 5 Priority

String Alarm 6 Priority

Specifies the priority of the point’s alarms.

Option is 0 to 99, with 99 being the highest.

In the CygNet Standard Point Scheme (0), alarm priorities are categorized as follows:

  • 0 - 24 Low
  • 25 - 49 Medium
  • 50 - 74 High
  • 75 - 99 Critical

0

Report To CAS

Select to reporting point alarms to the Common Alarm Service (CAS). Options are 0 (No) or 1 (Yes). The individual alarm bits must be enabled.

0 (No)

Report To GNS

Select to report point alarms to the General Notification Service (GNS), which will send notifications when an alarm bit is set/reset. Options are 0 (No) or 1 (Yes). The individual alarm bits must be enabled.

0 (No)

GNS ID

Select the ID of the GNS record to use for the notification regarding the alarm. The record type must be "Event" or "Unspecified." Click to select a GNS ID. See Configuring a GNS Record for information about setting up GNS IDs.

Blank

Delay Reporting

Select to delay reporting of the alarm to the CAS or to the GNS for some period of time to see if the point goes out of alarm. Options are 0 (No) or 1 (Yes). The individual alarm bits must be enabled.

0 (No)

Delay Value

Specify the amount of time to delay reporting alarms or processing notifications. The countdown begins when the alarm bit gets set. When set, that delay time governs all delay times for the point. Click … to enter the reporting delay value.

The format is as follows:

  • hh:mm:ss (for values up to 18 hours: 0-17 hours, 0-59 minutes, 0-59 seconds)
  • DD:hh:mm (for values up to 40 days: 0-39 days, 0-23 hours, 0-59 minutes)
  • Y:DDD:hh (for values up to 7 years: 0-6 years, 0-364 days, 0-23 hours)

00:00:00

(hh:mm:ss)

Back to top